Can an EZ Go charger be plugged into a 15 amp GFCI plug?
Just purchased a new golf cart. My question is....can I just plug the charger into a normal 15 AMP GFCI plug in my garage or do I have to change the CB in the main house panel to a 20 AMP CB to accommodate the charger?
|
Today | |
Sponsored Links
__________________
This advertising will not be shown in this way to registered members. Register your free account today and become a member on Buggies Gone Wild Golf Cart Forum |
|
05-29-2014, 01:48 PM | #2 |
Not Yet Wild
Join Date: Mar 2014
Location: Gulf Breeze Florida
Posts: 68
|
Re: Can an EZ Go charger be plugged into a 15 amp GFCI plug?
Mine would pop the GFI every time. I put in a 30 amp breaker and a dedicated circuit and no more problems.
|
05-29-2014, 03:42 PM | #3 |
Gone Wild
Join Date: Jan 2014
Location: South Georgia
Posts: 1,120
|
Re: Can an EZ Go charger be plugged into a 15 amp GFCI plug?
You should be able to plug it in the GFI. If it trips you have a ground fault in the equipment. A golf cart charger does not draw but about 7 amps @120 v.
|
05-29-2014, 07:45 PM | #4 |
Getting Wild
Join Date: Sep 2011
Location: watertown ct
Posts: 103
|
Re: Can an EZ Go charger be plugged into a 15 amp GFCI plug?
Mine is and it works fine
|
05-29-2014, 08:15 PM | #5 |
Happy Carting
Join Date: Dec 2007
Location: Southern California
Posts: 73,417
|
Re: Can an EZ Go charger be plugged into a 15 amp GFCI plug?
Yes but no extension cords
A 15a household circuit is typically 14g wire. 20a (dedicated appliance, garage, or outdoor) is 12g. Remember the closer you are to the main panel the less amperage drop you will experience. RM is correct about the draw. The problem is not the charger but the hair dryer somebody just turned on in the bathroom on the same GFI. LOL |
05-30-2014, 12:00 AM | #6 |
Not Yet Wild
Join Date: May 2014
Location: Burlington Ontario Canada & Mesa Arizona
Posts: 3
|
Re: Can an EZ Go charger be plugged into a 15 amp GFCI plug?
Thanks for the input. My concern is when I switched off the breaker to change the plug, it also shut off other things in my house, i.e. modem, router, tv, cable box, sound bar, etc. My concern is when I add the extra load of a golf cart charger, will it be too much for the 15 amp breaker to manage? Should I start lining up an electrician to change the breaker?
|
05-30-2014, 07:34 AM | #7 |
Gone Wild
Join Date: Sep 2012
Location: Savannah, GA
Posts: 2,760
|
Re: Can an EZ Go charger be plugged into a 15 amp GFCI plug?
It is nice to have the home outlet for a cart charger on a dedicated circuit. That usually isn't possible so a lightly used circuit is usually selected. Sounds like you are on a well used outlet. Try another one if possible that isn't as burdened.
You also cannot just put in a bigger circuit breaker either. The house wiring and outlets need to match the rating of the breaker. For 110vac outlets that is usually 15A or 20A. |
05-30-2014, 08:22 AM | #8 |
Gone Wild
Join Date: Jan 2014
Location: South Georgia
Posts: 1,120
|
Re: Can an EZ Go charger be plugged into a 15 amp GFCI plug?
Why don't you just try it and see? If the 15 amp breaker trips then upgrade it. If your house circuit has 14 gauge wire you don't want to replace a 15 amp breaker with a 20 amp one.
|
05-30-2014, 10:38 AM | #9 |
Not Yet Wild
Join Date: May 2014
Location: Burlington Ontario Canada & Mesa Arizona
Posts: 3
|
Re: Can an EZ Go charger be plugged into a 15 amp GFCI plug?
Thanks for the info. Ill give it a try. Unfortunately, out garage only has one plug. Grrrrrr :-)
|
05-30-2014, 11:34 AM | #10 |
Gone Mad
Join Date: Oct 2009
Location: Buford, GA
Posts: 8,988
|
Re: Can an EZ Go charger be plugged into a 15 amp GFCI plug?
Mine has 4 20 amp GFCI outlets, and I've never had any problems. However, 4 just ain't enough, so I added an additional 22 wire-mould non-GFCI outlets on the front of my work bench. All outlets in a garage, bathroom, kitchen, and outdoors "should" be GFCI, and this can be done at the breaker or the outlet. My 22 non-GFCIs are for playing with electrically "leaky" things.
|
|
|
Similar Threads | ||||
Thread | Forum | |||
Club Car will only run with Charger Plugged in | Electric Club Car | |||
charger reads 6 when plugged in | Electric Club Car | |||
charger will not come on when plugged into cart 48 ds 95 cc | Electric Club Car | |||
Charger does not start when plugged in | Electric Club Car | |||
charger will not kick on when plugged in | Electric EZGO |