Re: Xct400 error code
Quote:
However, there should be a diode (6A 660V) connected between the solenoid's large terminals to prevent the controller from getting spiked with high voltage if the solenoid contacts open during regen braking. The banded end of this diode connects to the solenoid's battery side large terminal. This is in addition to the diode between the solenoid's small terminals. When the cart misbehaves, check the voltage on Pin-5 and Pin-9. Both should have battery pack voltage as long as the Run/Tow switch is in Run and no charger is connected to cart. |
|
Today | |
Sponsored Links
__________________
This advertising will not be shown in this way to registered members. Register your free account today and become a member on Buggies Gone Wild Golf Cart Forum |
|
10-07-2018, 06:11 PM | #12 |
Not Yet Wild
Join Date: Feb 2017
Posts: 69
|
Re: Xct400 error code
Ok, I have the diodes in place. I will check that voltage when it acts up again. Thank you for the info JohnnieB.
|
|
|